I have a client whom recently had some electrical work done. The contractor installed enclosed breaker (480V, 3-phase, 400A) in an enclosure of which the cover is secured with bolts and nuts. The Owner is wondering what type of enclosure this is and why?

Best I can tell it is GE arc flash rated enclosure. the front cover is literally secured with about 5 threaded bolts w/nuts on each side.

Anyone know what is the purpose of such an enclosure?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: arc flash enclosure
PostPosted: Thu Jan 07, 2021 2:45 pm 
Plasma Level
User avatar

Joined: Wed May 07, 2008 5:00 pm
Posts: 881
Location: Rutland, VT
sounds like he just used an enclosure for a stand alone breaker. Not unusual as I have seen that type of setup before in lieu of a fused disconnect switch. I have also seen that type of setup used separate from an MLO MCC to reduce the arc flash at the MCC.

_________________
Barry Donovan, P.E.
www.workplacesafetysolutions.com


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: arc flash enclosure
PostPosted: Thu Jan 07, 2021 6:12 pm 
Arc Level

Joined: Tue Jan 13, 2009 5:00 pm
Posts: 631
If the cover requires tools to open and access and operate the breaker, it sounds like it may be a code violation.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: arc flash enclosure
PostPosted: Mon Jan 11, 2021 8:38 am 

Joined: Thu Feb 17, 2011 11:55 am
Posts: 3
Location: Cincinnati, OH
It is possible that the enclosure is attempting to do something similar to enclosures used in Classified Area i.e. Class I Division1 by venting and cooling any any gases heated during an arc flash event via the gap between the cover and the enclosure box while maintaining the structural integrity of the enclosure.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: arc flash enclosure
PostPosted: Mon Jan 11, 2021 9:06 am 

Joined: Tue May 29, 2018 8:19 am
Posts: 45
Yes, could be hazardous location enclosure. Is there nameplate? Can you post a photo?

_________________
Alan Lehman


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883