PostPosted: Thu Jun 10, 2021 3:04 pm 

Joined: Mon Sep 02, 2019 12:44 pm
Posts: 2
I am responsible for amongst a number of other things -175 aging Concrete batching plants around Australia - all are supplied from a pole mounted transformer via fuses at 400V.
The sites range in size according to Load ratings from 150A to 700A at approximately 50 A increments with the majority of the sites being rated at 250A.
All sites are basically of the same configuration; and typically consist of a main Switch feeding an MCC which feeds 2 conveyors (11kW ea) a mixer (45kW), Compressor(37kW), 3 Silos, Plant lighting and an admin office and a batching control room.
We just cannot afford the $4000 per site for an Arc Flash Study!
I was hoping to use the IEEE 1584 spreadsheet in order to perform generic AF calculations on typical sites ranging from 150A;200;250;300; ...700A) to determine the worst case scenario per rating and whether I could apply these results to all plants of the same load?

Any advice would be most welcome.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Multiple sites with low load ratings
PostPosted: Fri Jun 11, 2021 11:59 am 

Joined: Thu Apr 18, 2019 11:42 am
Posts: 49
Perform generic studies at your own risk. Differing transformer impedances, available fault currents from the utility, etc. My opinion, but I don't think that is a good idea.

Mike


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Multiple sites with low load ratings
PostPosted: Sat Jun 12, 2021 1:51 am 
Sparks Level
User avatar

Joined: Tue Apr 17, 2012 8:19 am
Posts: 244
Location: Charlotte, NC
mpparent wrote:
Perform generic studies at your own risk. Differing transformer impedances, available fault currents from the utility, etc. My opinion, but I don't think that is a good idea.

Mike


Agreed. If you don't want to pay for a professional to do the study, you will need to do the study yourself (hopefully by someone who knows how to do it). There is software available - likely at a lower overall cost than paying for each individual site. There are too many possible variables to generalize given a plant's amp load or kilowatt rating.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Multiple sites with low load ratings
PostPosted: Sun Jun 13, 2021 3:54 pm 

Joined: Mon Sep 02, 2019 12:44 pm
Posts: 2
Thanks very much for taking the time to respond I was hoping for someone who had been faced with the same dilemna - I will gather as much detailed info as possible and do the spreadsheet calcs, ask for a professional opinion on the results and then take action.
Hard to motivate and justify a spend of over $700k when there have been no incidents on 175 sites spread around the country in over 30 years..


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883