PostPosted: Tue Feb 15, 2022 6:43 am 

Joined: Mon Mar 09, 2020 9:27 am
Posts: 30
I am going through prints to build my preliminary SKM model and came across an autotransformer that is being used to adjust voltage possibly? The notation on the prints is "Auto transformer +10% voltage range". i have not worked with autotransformers, but that is my understanding of them. Its feeding and old theatrical dimmer rack system.

My questions is, how do they effect short circuit/Arc flash? Would this be modeled as an impedance device? What special considerations needed to be taken with them? SKM does not have a component for an autotransformer as far as i can see. So i am curious.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Autotransformers and Arc Flash
PostPosted: Mon Mar 28, 2022 7:56 am 
Arc Level

Joined: Thu Jan 10, 2008 8:49 pm
Posts: 514
Location: New England
The secondary winding is in series between the source and load. The primary winding is in parallel between line and neutral.
So its like having a reactor(or a large inductor) in the circuit. The problem is that its difficult to get specifications on just the secondary winding.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Autotransformers and Arc Flash
PostPosted: Mon Mar 28, 2022 2:06 pm 
Arc Level

Joined: Tue Jan 13, 2009 5:00 pm
Posts: 584
An auto transformer has a single winding. An auto is like any other transformer, it trades voltage for current. Neglecting the impedance of the transformer, a 10% boost in voltage will result in a 10% drop in fault current. Fault current will drop further due to transformer impedance. A two winding transformer model might be adaptable if you could enter a sufficiently low impedance. But is this a fixed 10% booster, or is it a step voltage regulator? If it's a regulator, it will have multiple steps between 0 and 10%. When on neutral, a voltage regulator will have no effect on fault current.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Autotransformers and Arc Flash
PostPosted: Mon Apr 11, 2022 8:16 am 
Arc Level

Joined: Thu Jan 10, 2008 8:49 pm
Posts: 514
Location: New England
I had this issue a few years ago. I went to another site for help. This is the response.

https://www.eng-tips.com/viewthread.cfm?qid=386462

the one suggestion to measure impedance was a good one if you have the test capability. This is the way manufacturers measure impedance so there is no reason you can't do it yourself. Use a variac to limit input voltage into a shorted secondary and measure current.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883