 Post subject: Condition of maintenance
PostPosted: Sun Jun 04, 2023 12:07 pm 
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 2178
Location: North Carolina
Is it just me or is the degree of waffling on this topic ridiculous? Am I the only one that thinks 70E is out to lunch? They can’t even define it! I’ll bet most of them have never smoked a breaker on a high current test set either.

I’ll go out on a limb and state that electrical equipment isn’t inherently dangerous. If it was that would be an invitation to financial ruin for manufacturers and it wouldn’t be on the market. The lawyers would see to that.

So manufacturers believe it or not do address this, though maybe not to the likings of the NETA crowd. For instance for molded case breakers the standard is to exercise (operate) it once a year and do a visual inspection once a year and after every trip. This is a far cry from what NETA states but that’s a standard written by testing companies to promote excessive and ridiculous testing not necessarily supported by science. And presumably this goes back to the idea that again, it’s not inherently dangerous.

70E does not provide procedures for not maintaining equipment nor analyzing the results for improperly maintained equipment No one does. Again this is sticking your neck out there. So the idea of putting an onus on the people working on the equipment to verify proper maintenance is done is crazy talk. You do NT know that and often you can’t. You can do some external inspection but it is unrealistic to verify “condition of maintenance” but honestly hidden failures are…hidden. It’s not possible for someone working on equipment to have deep engineering knowledge in most cases. That stuff should be a condition to 70E. If you don’t maintain it, 70E does not apply.

So with that in mind a very simple list of visual inspection results. Is it tripped or off? Is there burn marks, liquids rolling out, etc.? Are there water spots or other signs of environmental contamination or physical damage? If so, it’s not normal work.

So why insist end users must perform some magic incantation to determine factors they can’t possibly determine?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Condition of maintenance
PostPosted: Tue Jun 06, 2023 8:21 am 
Sparks Level

Joined: Thu Apr 18, 2019 11:42 am
Posts: 175
Paul,

I have had issues w/ the guidance we have through 70E as well. I would also add that IMHO, some of the recommendations in NETA and 70B are outdated in terms of maintenance, e.g. 1 yr exercising requirement of MCCBs. New manufacturing techniques would seem to indicate that guidance is in need of re-evaluation.
To your point, if testing is the only way to minimize breaker failures for example, then how far do you go? It isn't reasonable to test 20A/3p breakers, esp. for large facilities.

Interested in your viewpoint,

Mike


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Condition of maintenance
PostPosted: Mon Jun 12, 2023 5:36 am 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 488
Location: Indiana
70B-2023 supposedly has had some updating done but I have not reviewed it beyond what is mentioned in this article:

https://www.eaton.com/content/dam/eaton ... 024Xen.pdf

_________________
SKM jockey for hire
PE in 17 states


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Condition of maintenance
PostPosted: Mon Jun 12, 2023 1:36 pm 
Sparks Level

Joined: Thu Apr 18, 2019 11:42 am
Posts: 175
A lot of "shall" in there. As you might expect, questions arise as you read it, e.g. MCCB testing required down to what level/ampacity/pole(s) of breaker? At first glance, it's silly to test 20A/1p breakers, but there is no distinction between sizes, etc.

I have to admit I only skimmed the changes, but it is a bit scary. I'm not diminishing the need for maintenance but I've always thought this doc/guidance is overkill.

Mike


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Condition of maintenance
PostPosted: Fri Jun 23, 2023 10:18 am 
Sparks Level

Joined: Fri Sep 28, 2018 7:32 am
Posts: 57
Location: Sioux Falls, SD
It is my understanding that the latest edition of 70B provides guidance for users/owners to assess the equipment and determine what tasks are to be done at what interval at each device. You may decide to injection test all breakers 400amps and larger. The key is that you are using good judgement in your decisions and can defend the Electrical Maintenance Program if an event occurs. i.e. you cannot just say we're not going to injection test or maintenance anything.

I direct customers to injection test larger breakers with electronic trip units as well as any larger thermal magnet breakers that are critical to the process or are difficult to obtain if they fail.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883