Does anyone know the purpose for the note on 130.5(G) in NFPA 70E, where it prohibits the use of table 130.7(C)(15)(c) in specifying PPE categories. As an example, if the IE analysis shows we have 30 cal/cm^2, why is it prohibited to look at this table and know that we need to specify category 4 clothing?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: NFPA 70E. 130.5(G) Note
PostPosted: Mon Apr 28, 2025 5:57 am 
Sparks Level

Joined: Thu Apr 18, 2019 11:42 am
Posts: 137
You would use table 130.5(G) as the intent is to dress for the actual IE, since you calculated it. The other table you mention is for risk based analysis only (keeping in mind the bounds/requirements in the footnotes).