 Post subject: Arc Gap for Overhead Power Lines
PostPosted: Tue Sep 26, 2023 8:13 am 

Joined: Tue Sep 26, 2023 7:58 am
Posts: 1
How do you determine the Arc Gap for overhead power lines? We have always used 6" for 15kV per the IEEE 1584 Table 8. However, OSHA 1929.960 states that for single conductors in air, 15kV and less (and > 15kV) for a three-phase arc the "Phase conductor spacing" should be used. Typical spacing on an overhead power line would be around 36". This would produce values far greater than has been the "industry standard" to date. What are your thoughts on this?

One thing to note is that the NESC Table 410-2 is based off of a 4" gap for 15.1kV to 25kV. So it appears that NESC was not on board with OSHA's recommendation to use the conductor spacing for Arc Gap.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Gap for Overhead Power Lines
PostPosted: Tue Sep 26, 2023 4:00 pm 
Arc Level

Joined: Tue Jan 13, 2009 5:00 pm
Posts: 626
Take a look at the notes for Table 6 at https://www.osha.gov/laws-regs/regulations/standardnumber/1910/1910.269AppE. I think you'll see similar values to NESC.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883