It is currently Tue Oct 13, 2026 4:09 am
 Post subject: how can I detect the arc flash level at the VSD point in SKM
PostPosted: Sun Jan 28, 2024 3:30 pm
Hi,
Why SKM doesn't to detect the arc flash level at the VSD bus however it can detect the CB's bus, the bus before and the bus after VSD? is there is a way to able to detect the fault level at the VSD bus?
 Post subject: Re: how can I detect the arc flash level at the VSD point in
PostPosted: Sun Jan 28, 2024 3:42 pm
Not sure I'm interpreting your question correctly but if so you can add a bus to represent the line side of the drive then connect the drive to that bus. You'll have to give the bus some enclosure properties if you don't want to use panel as the default.
PostPosted: Tue Feb 20, 2024 4:44 am
Yes, I had to add a bus before the VSD and It worked!
I really appreciate the help.
Cheers