 Post subject: Arc Flash requirements for 480 V receptacles
PostPosted: Wed May 01, 2024 8:56 am 

Joined: Wed Apr 06, 2011 2:20 pm
Posts: 23
Is there any Arc flash analysis requirement for 480V receptacles ! Anyone has any comments!


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash requirements for 480 V receptacles
PostPosted: Mon May 06, 2024 3:16 pm 
User avatar

Joined: Mon May 25, 2015 1:17 pm
Posts: 18
Location: Northern California
As they are not worked on energized I would say this is a clear no.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash requirements for 480 V receptacles
PostPosted: Tue May 07, 2024 5:45 am 

Joined: Fri Sep 24, 2021 7:17 am
Posts: 39
Sometimes they're nice to see on a single line diagram though


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash requirements for 480 V receptacles
PostPosted: Tue May 07, 2024 2:45 pm 
Arc Level

Joined: Tue Jan 13, 2009 5:00 pm
Posts: 631
GaryPC wrote:
As they are not worked on energized I would say this is a clear no.

And they are considered energized until tested to prove otherwise. Sounds to me like a clear yes.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash requirements for 480 V receptacles
PostPosted: Wed May 08, 2024 10:55 am 
Sparks Level

Joined: Fri Sep 28, 2018 7:32 am
Posts: 63
Location: Sioux Falls, SD
If personnel will be making/breaking a connection at the receptacle while energized or if the receptacle will be used to verify zero energy then I would say yes. Shortly after the 2018 update to 1584 was released I found a 208V receptacle in a kitchen area of an industrial plant. When modeled using HCB it exceeded 2kA and had a surprisingly high IE. I'm wanting to say > 4 calories. This caught my attention as it wouldn't be uncommon for an issue to occur and an appliance repairman arrived who may not be overly knowledgeable of arc flash hazards and not properly protected. He could make/break the connection while crouching down in a tight space limiting his egress.

I would NOT overlook AF hazards at receptacles!


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours