It is currently Wed Oct 28, 2026 2:50 pm



Post new topic Reply to topic
Author Message
 Post subject: Where to disconnect power for an ESWC
PostPosted: Tue Oct 08, 2024 10:10 am 
Sparks Level

Joined: Sat Apr 04, 2009 9:50 pm
Posts: 122
Location: San Antonio, TX
To achieve an ESWC, all sources of electrical power that supply electrical equipment need to be disconnected.

I understand we cannot use the main overcurrent protection device from the electrical equipment, but an upstream disconnecting means.

Otherwise, you will still have power to the electrical equipment on the line side of this main overcurrent protection device.

I can't find a reference to this in the NFPA 70E. Where does it specifically say that we can't use the main OCPD of the electrical equipment to disconnect the power to this equipment?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Where to disconnect power for an ESWC
PostPosted: Wed Oct 09, 2024 5:27 am 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 499
Here's one opinion on it:

https://www.70econsultants.com/is-elect ... isconnect/

It basically says that it depends on if the line side conductors and lugs are exposed as well as what you are doing.

_________________
Retired but I might visit once in awhile


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883