 Post subject: Older Equipment Exclusion
PostPosted: Tue Oct 13, 2009 8:27 am 
Offline

Joined: Fri Jul 31, 2009 8:28 pm
Posts: 6
I seem to recall reading that if equipment was older than a certain date ( early 90's rings a bell) you are not required to perform an arc flash analysis. Has anybody else ran across this? If so where is it found?

Thanks for your help. Thank you to those you have answered my previous questions as well.

Derrick


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Oct 13, 2009 9:41 am 
Offline
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
Scheids78 wrote:
I seem to recall reading that if equipment was older than a certain date ( early 90's rings a bell) you are not required to perform an arc flash analysis. Has anybody else ran across this? If so where is it found?

Thanks for your help. Thank you to those you have answered my previous questions as well.

Derrick


Never heard that one, makes no sense at all.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Oct 13, 2009 10:13 am 
Offline

Joined: Fri Jul 10, 2009 10:14 am
Posts: 18
Location: West Central, OH
OSHA 1910 Subpart S

This is a part of the revised OSHA code that we are using to require all of our sites complete the basic electrical studies (arc flash optional if you fit on the tables). I have only included a portion of the OSHA code

1910.302(b)(1)
Requirements applicable to all installations. The following requirements apply to all electrical installations and utilization equipment, regardless of when they were designed or installed:

┬ž 1910.303(b) -- Examination, installation, and use of equipment

1910.303(b)(4)
Interrupting rating. Equipment intended to interrupt current at fault levels shall have an interrupting rating sufficient for the nominal circuit voltage and the current that is available at the line terminals of the equipment. Equipment intended to interrupt current at other than fault levels shall have an interrupting rating at nominal circuit voltage sufficient for the current that must be interrupted.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Oct 13, 2009 10:22 am 
Offline

Joined: Fri Jul 31, 2009 8:28 pm
Posts: 6
I agree it does not make sense. Thats why I was trying to figure out where I could of read it. Thanks


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Oct 13, 2009 11:28 am 
Offline

Joined: Thu Nov 15, 2007 7:58 am
Posts: 33
Location: NY
There is an OSHA reg that pertains to older equipment. But it has to do with the ability to accept a lock for lockout\tagout purposes .All newer equipment must be capable of accepting a lock.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883