When looking at arc flash in regards to large three phase UPS systems, curious to how others have modeled them in various software's as a UPS output of a 480V or even 208V UPS? there is a time prior to the UPS entering bypass mode? How does the UPS / inverter rectifier handle this?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Nov 23, 2009 9:22 pm 
Offline

Joined: Mon Jan 26, 2009 5:00 pm
Posts: 46
Location: Midwest
Mike
most modules are pretty soft and have limited, short duration clearing. I would find a value in the specs that the system can put out for 2 sec duration. Use that in all possible combinations of modules in service. it's not enough to trp anything big instantaneous, but smoke a pdu and burn your eyebrows, probably.

For hard faults, the thing is going into bypass real fast, probably fast enough to neglect the half cycle of module and static transfer. Just model that as being hardwired to bypass and utility then repeat for gens.

I'm also going to try not to model the effects of an upstream closed transition transfer. Sorry skm only gives me 10 scenarios and I blew them all on n+1 modules and generators!

Steve


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Nov 24, 2009 6:23 am 
Offline
Sparks Level

Joined: Tue Feb 24, 2009 7:05 am
Posts: 252
What about the battery side of a large UPS? A lot of energy is stored in them, and there are no fuses/CB between the cells, or between the of a single cell, so the clearing time can be long even though the voltage can be only 2 VDC.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883