Author:  Brodie [ Fri Dec 25, 2009 5:05 pm ]
Post subject:  AIC Ratings

Several Circuit Breakers failed on Short Circuit Study,at what point if any is this an option to replace? :confused:

Attachments:
MVC-014S.JPG
MVC-014S.JPG [ 19.34 KiB | Viewed 1677 times ]

Author:  Zog [ Fri Dec 25, 2009 6:13 pm ]
Post subject: 

Brodie wrote:
Several Circuit Breakers failed on Short Circuit Study,at what point if any is this an option to replace? :confused:


Reducing the fault current sometimes is a better option, but if this is all you have failed you can easily upgrade these to higher interupting breakers, we provide these upgrades everyday and give exchanges for your old ones.

Author:  short-circuit52 [ Fri Dec 25, 2009 7:13 pm ]
Post subject: 

Are the failed breakers rated SC symmetrical or asymmetrical fault current?