 Post subject: Replacing Fuses
PostPosted: Tue Jan 26, 2010 10:46 am 

Joined: Thu Feb 28, 2008 6:24 am
Posts: 9
Recently we had an issue with replacing a european fuse block and fuses with a North American style (Bussman Class J 600V 60A 3PH). My boss was concern that since we had a Arc Flash audit and machining had their Category Rating it may change the machine Arc Flash rating.

This long as we match the same fuse rating with the original fuses, shouldn't this be not an issue?

rmonroe


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Jan 26, 2010 11:34 am 
Sparks Level

Joined: Wed Jan 28, 2009 2:19 pm
Posts: 73
Location: Georgia
The boss is right. Even replacing a Ferraz A6D fuse with a Ferraz TRS fuse with the same amp rating will affect the arc flash ratings. These are both time delay fuses.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Jan 26, 2010 3:15 pm 
Sparks Level

Joined: Tue Feb 24, 2009 7:05 am
Posts: 252
It also depends on whether those fuses being replaced were the one clearing the arc flash fault or not.

Let's say you're talking about a machine panel. If those fuses are the OCPD at the entrance of the panel (fused disconnect or otherwise), then an arc flash study for that panel shouldn't use those as the interrupting OCPD as the fault can be upstream of those fuses but still in the enclosure (ie, on the line side of the fuses).

If the category rating was for a secondary panel/junction box/motor box/etc. of that same machine (where the fuses you want to replace are the main OCPD), then it might affect the category rating as the TCC is most likely not the same.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Jan 27, 2010 12:09 pm 
Sparks Level

Joined: Wed Jan 28, 2009 2:19 pm
Posts: 73
Location: Georgia
Yes. Replacing fuses will not affect the arc flash rating of the panel that contains these fuses. It is the downstream panels that can be affected.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883