 Post subject: Bus Gap on 2000kVA transformer secondary
PostPosted: Wed Sep 23, 2020 8:00 am 

Joined: Tue Sep 22, 2020 10:53 am
Posts: 3
We are performing a study using the IEEE 1584 - 2018 in SKM and when we run the AF calc a note is generated stating that the bus gap is outside of the IEEE 1584 range on the secondary side of a 35kV:480V transformer. Looking at the transformer secondary, the gap between phase conductors is about 6" (154mm) which is typical for this type of equipment so I am confused as to what the issue is. Any suggestions?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Bus Gap on 2000kVA transformer secondary
PostPosted: Wed Sep 23, 2020 2:12 pm 

Joined: Thu Apr 18, 2019 11:42 am
Posts: 27
Take a look at the NESC.

Mike


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Bus Gap on 2000kVA transformer secondary
PostPosted: Thu Sep 24, 2020 4:54 am 

Joined: Tue Sep 22, 2020 10:53 am
Posts: 3
mpparent wrote:
Take a look at the NESC.

Mike


I don't have that in front of me at the moment (hard copy at the office). Could you summarize?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Bus Gap on 2000kVA transformer secondary
PostPosted: Sat Sep 26, 2020 12:51 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1517
Location: Scottsdale, Arizona
NovaTom wrote:
We are performing a study using the IEEE 1584 - 2018 in SKM and when we run the AF calc a note is generated stating that the bus gap is outside of the IEEE 1584 range on the secondary side of a 35kV:480V transformer. Looking at the transformer secondary, the gap between phase conductors is about 6" (154mm) which is typical for this type of equipment so I am confused as to what the issue is. Any suggestions?


I was conducing arc flash testing years ago on a padmount transformer / 480 volt side. I could not get it to sustain (don't use that statement as a formal statement) so I ended up bridging the gap with copper bus to get an IEEE 1 inch gap. Don't forget an arc flash could be from a dropped tool which will (initially) create a gap much smaller than 6 inches.

NESC

The 2017 NESC Table 410-2 for (arc rated) clothing systems uses the following gaps:
1 kV - 15 kV = 2 inches
15.1 kV - 25 kV uses 4 inches

For Pad mounted transformer up through 600 volts, NESC Table 410-1 references a technical paper by a couple of friends/colleagues Arc Flash Testing of Typical 480-V Utility Equipment Marcia Eblen and Tom Short. Their results indicate they could not sustain an arc flash on the secondary of the transformer and the NESC table indicates a maximum arc rating of clothing at 4 cal/cm^2 as a result of their finding.

Note: This is NOT an interpretation or recommendation - just referencing other work/standards.

Hope it helps.

btw, I can ask this as the "Question of the week" next week! - Watch this space.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Bus Gap on 2000kVA transformer secondary
PostPosted: Mon Sep 28, 2020 12:21 pm 

Joined: Tue Sep 22, 2020 10:53 am
Posts: 3
Thanks for the reply Jim! I find it interesting that there seems to be this gap (pun intended) in 1584 and the results of the Elban/Short paper. In SKM, when we have the bus gap at 153mm, the AFIE is 20.8cal/cm^2 (Lee equation used); when the bus gap is set to 76mm, the AFIE is 71.2cal/cm^2; but the NESC says regardless of the bus gap - it will be no more than 4cal/cm^2. For the sake of our clients and future studies, how do people generally report the AFIE for the secondary side of a MV-LV pad mounted transformer? Do most just take the conservative approach and list the higher value on the labels?


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883