I was asked to provide labels on the new equipment that was installed.
I have the utility details, MSBA details and I have the panel details. Do I need to model the whole Switchboard in SKM or can I just model the Utility, MSBA- Main breaker, MSBA and the two new equipment?


Attachments:
MSBA.jpg
MSBA.jpg [ 661.79 KiB | Viewed 64204 times ]
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Modeling new equipment.
PostPosted: Thu Feb 06, 2025 8:51 am 
Sparks Level

Joined: Thu Apr 18, 2019 11:42 am
Posts: 163
I think it depends. It looks like you have motor loads hanging off your main switchboard, so those could feed into faults at your new panels. If they are on VFDs, then maybe you don't have to model them as added short circuit contribution (unless they have a bypass, then maybe you do).

Mike


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Modeling new equipment.
PostPosted: Fri Feb 07, 2025 4:40 am 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 438
Location: Indiana
I agree with Mike's assessment. That is a small system and wouldn't take long to model. The time consuming part will be getting all the data.

_________________
SKM jockey for hire
PE in 17 states


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883