It is currently Wed Feb 18, 2026 1:12 pm
 Post subject: Bolted Pressure Switch
PostPosted: Mon Feb 16, 2026 11:23 am
any tips on modeling an Eaton bolted pressure switch? switchboard is using a BPS as the main device with ARMS mode. would this be modeled just as a fuse?
 Post subject: Re: Bolted Pressure Switch
PostPosted: Tue Feb 17, 2026 7:18 am
I think Eatons' offering is actually an arc reduction relay tied to the BPS. In my opinion, you'll model two things:
1. Fuse
2. The arc reduction relay with trip times from the manufacturer. You may have to create your own library file for this one, unless SKM, Easypower, etc. have a model file you can use.
Mike