 Post subject: Substation Transformers - AF Boundary
PostPosted: Mon May 17, 2010 7:42 am 

Joined: Tue Mar 31, 2009 10:27 am
Posts: 6
Location: Norcross Georgia
This may be a dumb question, but I'll ask anyway.

Shouldn't the AF boundary be calculated and applied to substation type transformers (tranformers with exposed bushings)?

A example would be a utility substation feeding an industrial plant. Very large transformers installed in a small fenced area, with a parking lot and/or sidewalk next to the fence.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon May 17, 2010 7:48 am 
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 523
Location: Wisconsin
Don't_wanna_burn wrote:
This may be a dumb question, but I'll ask anyway.

Shouldn't the AF boundary be calculated and applied to substation type transformers (tranformers with exposed bushings)?

A example would be a utility substation feeding an industrial plant. Very large transformers installed in a small fenced area, with a parking lot and/or sidewalk next to the fence.


Yes it should when interaction is taking place.
If the substation is under the control of the facility, then NFPA70E applies.
If the substation is under the control of the utility, then the NESC applies.

Unless some one or something is interacting with the exposed conductors, arc flash boundaries are not applicable to someone 'passing by on the side walk', just like they are not for people passing an indoor metal enclosed substation.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Oct 12, 2010 8:25 am 
Sparks Level

Joined: Thu Oct 18, 2007 7:10 pm
Posts: 261
Location: NW USA
This could be rationalized to include all utility transformers however; there probably has not been a problem with these.

That is somewhat like requiring seat belts on school buses: it seems like sound reasoning yet there hasn't been a problem without.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883