wbd
|
Post subject: Downstream of VFD Posted: Thu Oct 14, 2010 3:20 pm |
|
| Plasma Level |
 |
Joined: Wed May 07, 2008 5:00 pm Posts: 881 Location: Rutland, VT
|
|
Hello,
I was curious to see how other people are handling equipment downstream of VFD's. I don't have much experience with VFD's but I would think that due to the nature of a VFD it would not support much of an arc due to rapid circuitry response.
Thoughts/comments/discussion?
_________________ Barry Donovan, P.E. www.workplacesafetysolutions.com
|
|
| Top |
|
 |
|
JJH
|
Post subject: Posted: Fri Oct 15, 2010 10:20 am |
|
Joined: Wed Jan 28, 2009 2:19 pm Posts: 74 Location: Georgia
|
|
I handle disconnects downstream of VFD's the same way as I handle them if there were no VFD installed. The VFD makes no impact on my study of downstream equipment. Most VFD's are non-regen and will not allow current from the motor to pass backward to the supplying bus.
|
|
| Top |
|
 |
|