 Post subject: Overdutied Device Interrupting Ratings
PostPosted: Thu Jul 15, 2010 7:49 am 

Joined: Mon Mar 16, 2009 10:43 am
Posts: 2
NFPA 70E says that "design" and "condition of maintenance" should be taken into account for arc flash hazard analysis.

For equipment with over-dutied interrupting ratings what is the proper approach for an arc flash hazard analysis? As in what was the intention of NFPA in incorporating design, or lack thereof, into the analysis?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Jul 15, 2010 10:58 am 
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
jkopinski wrote:
NFPA 70E says that "design" and "condition of maintenance" should be taken into account for arc flash hazard analysis.

For equipment with over-dutied interrupting ratings what is the proper approach for an arc flash hazard analysis? As in what was the intention of NFPA in incorporating design, or lack thereof, into the analysis?


I suume you mean your available fault current is > the AIC rating of your breaker? If so I would not assume that breaker is an OCPD at all.

The 70E is not a design or instalation standard, that is what the NFPA 70 is for (NEC).

Good question, interested to see what others do in this case.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Jul 15, 2010 1:37 pm 
Sparks Level

Joined: Sun Dec 23, 2007 1:44 pm
Posts: 348
Location: Charlotte, NC
If you cannot find an acceptable method to lower the available fault duty, then I would replace the equipment while there is still something to replace.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Jul 15, 2010 2:22 pm 
Sparks Level

Joined: Mon Mar 29, 2010 11:52 am
Posts: 110
Location: Yankton SD/ Lead SD
Zog wrote:
I suume you mean your available fault current is > the AIC rating of your breaker? If so I would not assume that breaker is an OCPD at all.

The 70E is not a design or instalation standard, that is what the NFPA 70 is for (NEC).

Good question, interested to see what others do in this case.


NFPA 70 should not be considered a "design standard". I would classify it more as a "minimum requirememnts installation guide".


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883