ekstra   ara
 Post subject: 3-Phase Transformer Model
PostPosted: Wed Jul 28, 2010 8:08 pm 

Joined: Wed Jul 21, 2010 7:54 am
Posts: 4
Location: OK
If I have a 300 kVA utility transformer bank made up of 3 single phase 100 kVA transformers each with an impedance of 1.9%, is the equivalent impedance of the 300 kVA transformer simply 3 x 1.9, or is it the square root of 3 times 1.9?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Jul 29, 2010 9:51 am 
Arc Level

Joined: Wed Jun 04, 2008 9:17 am
Posts: 428
Location: Spartanburg, South Carolina
RJohnson wrote:
If I have a 300 kVA utility transformer bank made up of 3 single phase 100 kVA transformers each with an impedance of 1.9%, is the equivalent impedance of the 300 kVA transformer simply 3 x 1.9, or is it the square root of 3 times 1.9?

1.9%. The impedance is a per phase value.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Jul 30, 2010 8:04 am 
Arc Level

Joined: Tue Jan 13, 2009 5:00 pm
Posts: 532
How are the transformers connected? Wye or delta?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sat Jul 31, 2010 10:42 am 

Joined: Wed Jul 21, 2010 7:54 am
Posts: 4
Location: OK
Connected delta-wye.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Aug 02, 2010 8:52 am 
Arc Level

Joined: Tue Jan 13, 2009 5:00 pm
Posts: 532
Edited: Sorry I misremembered. Connections make no difference. 1.9% using 100 kVA and line to neutral voltage to get ohms secondary equates to 1.9% using 300 kVA and line to line voltage.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Aug 03, 2010 6:38 am 

Joined: Fri Jan 30, 2009 10:04 am
Posts: 10
Location: Toronto
RJohnson wrote:
Connected delta-wye.


No matter how the 3 single phase transformer connected, the impedance should be the same as the single phase tested value


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Jun 07, 2011 12:32 pm 

Joined: Mon Apr 13, 2009 11:54 am
Posts: 8
Location: Midland, Tx
What is one of the transformers has a different nameplate impedance?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Jun 10, 2011 8:35 am 
Arc Level

Joined: Tue Jan 13, 2009 5:00 pm
Posts: 532
Then there is no equivalent three phase impedance.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sun Jun 12, 2011 6:08 pm 

Joined: Fri Jan 30, 2009 10:04 am
Posts: 10
Location: Toronto
Can 3 single phase transformers with different IZ% be connected to a transformer bank?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sun Jun 12, 2011 10:33 pm 
Sparks Level

Joined: Mon Mar 29, 2010 5:02 am
Posts: 136
J.T wrote:
Can 3 single phase transformers with different IZ% be connected to a transformer bank?


It is my understanding that they can be, but they still have to be within a very tight range..


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 10 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883