PostPosted: Wed Oct 20, 2010 8:57 am 
Sparks Level

Joined: Tue May 18, 2010 7:03 am
Posts: 53
Modelling a system with 3 single phase, 50 kva transformers, 2%Z each, set up as a 3 phase 150kva, 2%Z. Three phase available fault current of 2950A at 12kv. I'm getting fault currents of almost 21ka on the secondary side of the transformer. After 75 feet of aluminum quad service drop cable, the fault current is about 8.6ka. This is the first 208 system I've done so the fault currents seem high on the secondary side of the transformer and the drop in fault current seems high after the first cable.

Is there anything obvious here I'm missing?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Oct 20, 2010 4:22 pm 
Sparks Level

Joined: Tue Feb 24, 2009 7:05 am
Posts: 252
(Didn't ran actual calcs, just my feeling)

The %Z value is quite low (2%), so it's normal that the fault current at the secondary be on the high side. When you add the service drop cable, its impedance is probably quite high in comparison, so that's why you get such a drop in fault current after 75 feet.

Try the same calcs with a higher %Z: the fault current should be higher and closer after your 75 feet cable.
Try also with a way bigger cable: the drop should be quite smaller for the same 2% %Z.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Oct 21, 2010 5:18 am 
Sparks Level

Joined: Tue May 18, 2010 7:03 am
Posts: 53
Thank you for your comments. I dug around quite a bit in some old GE literature and found recommended impedances for studies. I think 2.4% was the number I found for the single phase pots. The 2% seems low but it is the number the utility provided. I played around quite a bit with different settings yesterday and the difference at the service entrance varied about 500 to 800 amps. I'll fuss with it some more. Thanks again.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Oct 21, 2010 5:29 am 
Plasma Level
User avatar

Joined: Wed May 07, 2008 5:00 pm
Posts: 822
Location: Rutland, VT
I just looked at some 50 kVA distribution transformers in stock (utility company) and they have an impedance of 1.4%. I would imagine that like most utilities, we need to keep losses down and the regulators want losses as low as possible.

_________________
Barry Donovan, P.E.
www.workplacesafetysolutions.com


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Oct 21, 2010 10:59 am 

Joined: Wed Jun 24, 2009 4:45 pm
Posts: 41
Location: WA State
mountaineer wrote:
The 2% seems low but it is the number the utility provided.


The 2% is a good number for a utility 50 kVA single phase pole type transformer 7200/12470Y-120/240V.

Our database has thousands of units all falling within the 1-3% range.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Oct 21, 2010 11:58 am 
Sparks Level

Joined: Tue May 18, 2010 7:03 am
Posts: 53
Thanks for all the replies - It makes me feel more confident about my results.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 6 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883