 Post subject: Short-Circuit Cutoff Levels
PostPosted: Wed Jun 11, 2008 11:08 am 

Joined: Tue Mar 25, 2008 1:00 pm
Posts: 32
I've been given a spec by a customer that states that short-circuit and arc flash analysis can be ignored below 14kA @480V and 10kA @ 208V. Would anyone know where these numbers came from?

My main question though is this: At the secondary of a transformer stepping from 480V to 208V, I am calculating a short-circuit current of 3kA, which should be excluded from the study by the spec, but I calculate an IE of 9.6 cal/cm^2, or PPE level #3.

Can anyone provide some insight here?
Thanks.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Jun 11, 2008 12:02 pm 
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
I have a guess. "Standard" AIC ratings for 208V breakers is (well used to be anyways) 10kA and 14kA for 480V. Higher fault currents require higher interuption ratings for the breakers. So maybe they are saying you dont need to do a S/C study below those values.

In a way that makes sense. However, that has nothing to do with arc flash, as you already found out. There can be some pretty series Ei's below the paramaters they set.

Unless I am missing something here, you need to go back to the customer and explain this. If they still want you to ignore the Arc Flash study below those levels, make them sign a waiver of liability.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Jun 12, 2008 10:37 am 
Arc Level

Joined: Thu Jan 10, 2008 8:49 pm
Posts: 498
Location: New England
Jim posted about an IEEE exception for 208V system fed by 125KVA and less transformer being excluded. I don't know about the 480V.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Jun 12, 2008 5:55 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1501
Location: Scottsdale, Arizona
I think Zog hit it on the head here. On the surface their logic of 14 kA and 10 kA might make sense but there is still some debate on how to handle low magnitude arcing currents. Most people have probably seen that very low currents can yield very long device clearing times which translates into more incident energy. The question is: is any of this realistic? There are many schools of thought such as the 125 kVA xfmr / < 240V exclusion clause in 1584, 2 second cut off, will the low level arc even sustain itself etc. Unfortuanely there is not a clear cut answer so people are "being creative" to justify minimizing the effort. If they get too creative, it might be difficult to explain in a legal setting.

_________________
Jim Phillips, P.E.
Brainfiller.com


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Jun 13, 2008 5:17 am 

Joined: Tue Mar 25, 2008 1:00 pm
Posts: 32
I'm glad its not just me. I'm just going to ignore their cutoffs and do the analysis for the whole system. Thanks everyone!


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Jun 13, 2008 6:28 am 
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
brainfiller wrote:
I think Zog hit it on the head here. On the surface their logic of 14 kA and 10 kA might make sense but there is still some debate on how to handle low magnitude arcing currents. Most people have probably seen that very low currents can yield very long device clearing times which translates into more incident energy. The question is: is any of this realistic? There are many schools of thought such as the 125 kVA xfmr / < 240V exclusion clause in 1584, 2 second cut off, will the low level arc even sustain itself etc. Unfortuanely there is not a clear cut answer so people are "being creative" to justify minimizing the effort. If they get too creative, it might be difficult to explain in a legal setting.


A friend of mine at Westex has done some arc flash testing at KEMA on 208V 125kVA and says he has seen arcs sustain themselves below the IEEE 1585threshold level, I dont remmember what Ei's he observed but they were high enough.

I guess there needs to be a cutoff point somewhere, and I am sure IEEE did thier homework on that level, but I can see that changing in the future. However, you need to find a point where the "Risk" level is low enough to ignore the "hazard", we will never, ever, be able to protect all workers from arc flash injuries. There is a chance, my computer battery could explode as I type this message, it has happened, but should we require PPE when working on a notebook PC?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Jun 24, 2008 10:58 am 
Sparks Level

Joined: Sat May 17, 2008 5:00 pm
Posts: 85
Zog, you used the key word. "Risk" If we are suppose to protect eveyone from everything, we'll be walking around in bubble wrap, kevlar, nomex and not be able to move. Risk and the practical side of all this needs still seems to need some work. :D


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 7 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883