| Author: | rks [ Wed Nov 24, 2010 11:26 am ] |
| Post subject: | NFPA70E; Annex D.7.5-Arc Flash Boundary Calc problem |
when i use the "theoretically derived equiation D.7.5B" to calculate AFPB distance and check my answer with SKM software value, my calculated distance is exactly one half the SKM value. anyone have a clue? |
|
| Author: | Robertefuhr [ Fri Nov 26, 2010 6:14 pm ] |
| Post subject: | |
Check the options settings for the SKM program. There are many settings that will affect the SKM calculations. |
|
| Author: | Jim Phillips (brainfiller) [ Sun Nov 28, 2010 4:44 pm ] |
| Post subject: | |
rks wrote: when i use the "theoretically derived equiation D.7.5B" to calculate AFPB distance and check my answer with SKM software value, my calculated distance is exactly one half the SKM value. anyone have a clue?
I am not sure why it is exactly 1/2 but I would expect the theoretical calculation to be higher. The empirically derived equation is from IEEE 1584 and is based on the normalized incident energy from a prior calculation step. The normalized Ei uses ARCING current and gap distances. The boundary calculation also uses an X distance factor which is a variation in the theoretical "squared" factor used to account for the incident energy dropping off by the inverse distance "squared". The X is based on the type of equipment and will be less than squared i.e. less than "^2" The theoretical calculation uses the BOLTED current and ignores most of the details described above. |
|