 Post subject: Cable sizes
PostPosted: Mon Apr 25, 2011 11:22 am 

Joined: Thu Apr 21, 2011 1:58 pm
Posts: 3
Hi,
This is my second thread to this forum.
My question concerns the field wiring sizes vs. the equipment wiring sizes. As an example, in our data center, we have 500 kcmil cable feeding our PDU's, which terminates to the line side of the main breaker. The factory wiring comes off the load side of the breaker as two 1/0 awg to the primary side of the transformer. According to the Liebert PDU manual they are alowed to down size because the cabinet is considered open air and they are allowed to use table 310.17. Does the SKM program take this into account or should the 500 kcmil size be used all the way to the primary side of the transformer?

Thanks!


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Apr 26, 2011 4:37 am 
Plasma Level
User avatar

Joined: Wed May 07, 2008 5:00 pm
Posts: 823
Location: Rutland, VT
I don't know about SKM, but in EasyPower when entering the conductor data, you can change the default ampacity rating of the conductor. Therefore special cases can be considered.

_________________
Barry Donovan, P.E.
www.workplacesafetysolutions.com


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Apr 26, 2011 8:15 am 
Sparks Level
User avatar

Joined: Mon Nov 23, 2009 6:37 am
Posts: 51
Location: Tampa, FL
awg wrote:
Hi,
This is my second thread to this forum.
My question concerns the field wiring sizes vs. the equipment wiring sizes. As an example, in our data center, we have 500 kcmil cable feeding our PDU's, which terminates to the line side of the main breaker. The factory wiring comes off the load side of the breaker as two 1/0 awg to the primary side of the transformer. According to the Liebert PDU manual they are alowed to down size because the cabinet is considered open air and they are allowed to use table 310.17. Does the SKM program take this into account or should the 500 kcmil size be used all the way to the primary side of the transformer?

Thanks!


On SKM you should be able to add a node at the junction of the two different cables and therefore consider the circuit as it is actually run rather than changing values of installed cables.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Apr 26, 2011 10:08 am 
Arc Level

Joined: Wed Jun 04, 2008 9:17 am
Posts: 428
Location: Spartanburg, South Carolina
The short section of 2-1/0 AWG will have little effect on the short circuit current and can be ignored for purposes of arc flash analysis.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883