It is currently Tue Nov 17, 2026 6:49 am
 Post subject: Utility X/R
PostPosted: Wed Jan 04, 2012 2:46 pm
Hi there. I saw the post about the service transformer X/R but I have a slight variation.
I have been trying to obtain the X/R for the source from the utility. They have provided the short circuit current but no impedance or X/R. The software assumes a value for me. Is the exact X/R that important for the arc flash study?
Thanks for the help!
PostPosted: Wed Jan 04, 2012 4:26 pm
Your case is similar to the other X/R question regarding transformers. Utilities don't alway have the X/R ratio (although many do). It will likley have a minimal affect on the arc flash study since the X/R defines the impedance angle not the actual impedance.
It plays a roll in how the X and the R are combined with other impedances. If you don't have an X/R a pretty common assumption is 12 or 15.
The inverse tangent of 12 is 85.2 degrees (the X/R is also the tangent of the impedance angle) so if you use 15 or even a larger value, you are talking about the last few degrees between 85.2 and 90 degrees which would be an impedance of all X and no R.
Good luck and check back if you need more help.