ekstra   ara
 Post subject: Microgrid simulation model for short circuit and arc flash
PostPosted: Tue Oct 18, 2011 8:32 am 

Joined: Fri Aug 27, 2010 1:15 pm
Posts: 2
Good morning everyone,

I have been discussing with etap and SKM whether or not they would be able to certify an accurate simulation model for a new electric utility 300KW microgrid.
Both etap and SKM have not yet replied.

There are several relays types that are not in their components library:

Relay type Description

37.............................. Under current relay

47.............................. Negative sequence voltage relay

51.............................. Time overcurrent relay

59.............................. Overvoltage relay

79.............................. AC reclosing relay

81o.............................Over frequency relay

81u.............................Under frequency relay.

All these relays are bundled together in a Beckwith M3410A control driving a digital control and protective relaying which will choose between a main 1200A CB and a bypass 1200A.

I have not studied the circuit in depth because I do not have a contract yet to start this project.

There are program for designing microgrid but I have not found simulation program for short circuit and arc flash.

My question: Do you know of any simulation program exclusive for microgrid short circuit and arc flash analysis?

Any help will be appreciated.

JuanA


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Oct 18, 2011 9:09 am 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1499
Location: Scottsdale, Arizona
Most of the major software companies have short circuit, coordination and arc flash modules already integrated together. Software like Easypower, SKM, ETAP etc. should also have various overcurrent (51) relays already in their data base. Since the other relays you list are not exclusively overcurrent, they will not be found in the software (unless they added something recently). I usually calculate these other relay settings separately.

_________________
Jim Phillips, P.E.
Brainfiller.com


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Oct 26, 2011 3:42 am 
Sparks Level
User avatar

Joined: Sat Jun 07, 2008 5:11 pm
Posts: 143
Location: Connecticut
I use Etap 7.5.2 and it has Beckwith M3410A relay in it's library along with the devices you listed. I recently did a coordination and SC study for a customer that has Cogen with four 4160v, 2500kW diesel generators burning methane gas from a landfill. The 4160v is stepped up to 13.8kV via xfmr to the utility grid. The PD's are Beckwith M3410A


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours