Hi there. I saw the post about the service transformer X/R but I have a slight variation.

I have been trying to obtain the X/R for the source from the utility. They have provided the short circuit current but no impedance or X/R. The software assumes a value for me. Is the exact X/R that important for the arc flash study?

Thanks for the help!


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Jan 04, 2012 4:26 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1501
Location: Scottsdale, Arizona
LHall wrote:
Hi there. I saw the post about the service transformer X/R but I have a slight variation.

I have been trying to obtain the X/R for the source from the utility. They have provided the short circuit current but no impedance or X/R. The software assumes a value for me. Is the exact X/R that important for the arc flash study?

Thanks for the help!


Your case is similar to the other X/R question regarding transformers. Utilities don't alway have the X/R ratio (although many do). It will likley have a minimal affect on the arc flash study since the X/R defines the impedance angle not the actual impedance.

It plays a roll in how the X and the R are combined with other impedances. If you don't have an X/R a pretty common assumption is 12 or 15.

The inverse tangent of 12 is 85.2 degrees (the X/R is also the tangent of the impedance angle) so if you use 15 or even a larger value, you are talking about the last few degrees between 85.2 and 90 degrees which would be an impedance of all X and no R.

Good luck and check back if you need more help.

_________________
Jim Phillips, P.E.
Brainfiller.com


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883