 Post subject: Scott Connected Tranfomer Model
PostPosted: Mon May 21, 2012 10:00 am 

Joined: Mon May 21, 2012 9:51 am
Posts: 1
Location: Philadelphia, PA
We have several two-phase transformers in our plant and I need to model them for our arc flash study. I found some old drawings that provide the following data:

2-167KVA TRANSFORMERS SCOTT CONNECTED
13.2 KV 3PHASE TO 240/480V 2PHASE

I am using ESA Easypower but any general guidence would be very helpful.

Thank you!


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sat May 26, 2012 2:53 pm 
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 2174
Location: North Carolina
Available arc flash models generally consider 3 phase only. Considering that the fault energy is identical for single or two phase cases with L-L faults, the 3 phase model results are still valid.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon May 28, 2012 2:58 pm 

Joined: Thu Feb 04, 2010 5:00 pm
Posts: 36
Location: Camp hill Pa
PaulEngr wrote:
Available arc flash models generally consider 3 phase only. Considering that the fault energy is identical for single or two phase cases with L-L faults, the 3 phase model results are still valid.

PaulEngr wrote:
Available arc flash models generally consider 3 phase only. Considering that the fault energy is identical for single or two phase cases with L-L faults, the 3 phase model results are still valid.

Soud Laskar wrote:
We have several two-phase transformers in our plant and I need to model them for our arc flash study. I found some old drawings that provide the following data:

2-167KVA TRANSFORMERS SCOTT CONNECTED
13.2 KV 3PHASE TO 240/480V 2PHASE

I am using ESA Easypower but any general guidence would be very helpful.

Thank you!


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Jun 04, 2012 10:06 am 

Joined: Wed Aug 31, 2011 5:26 am
Posts: 11
My initial thougth was "open Delta". However, admittedly I've never heard the term, "Scott Connected". Since I'm always eager to learn, I can't wait to fine out what that refers to! Thanks.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Jun 04, 2012 3:57 pm 
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 523
Location: Wisconsin
A Scott Connection involves the use of two transformers connected in a Tee arrangement which acts as if it was a delta-wye. The Scott connection was designed for going between 3-phase and 2-phase systems, although it has become synonymous with any "T" connection.

The T arrangement is very popular in small kVA ratings (i.e. <30kVA).
A 208Y120 output effectively requires one 240V winding tapped at 50% and 86.7% and the other tapped at 86.7% and 25%.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883