 Post subject: Software default inrush factor
PostPosted: Mon Jun 11, 2012 9:18 am 

Joined: Sat Nov 21, 2009 3:10 pm
Posts: 25
The software I use has a default inrush factor of 12. I have always used this default inrush factor for all my studies I have done. Recently I was told that the factor of 12 is not acceptable and that I should be using something more in the 6-8 range. Can anyone shine some light on this for me?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Jun 11, 2012 9:32 am 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1499
Location: Scottsdale, Arizona
6-8 is certainly on the low end. I have always used the following (based on my Square D upbringing :) )

Liquid Filled or Unknown Transformer = 12X
Dry Type = 10X
Cast Coil = 8X

However the actual inrush is also dependent on factors such as when in the voltage waveform the circuit is closed, past magnetizing history etc. so it is possible to have a lower inrush just based on these variables but the numbers above are what I use.

_________________
Jim Phillips, P.E.
Brainfiller.com


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Jun 11, 2012 9:42 am 

Joined: Sat Nov 21, 2009 3:10 pm
Posts: 25
Thanks for the reply. This helps!


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Jun 18, 2012 5:56 am 
User avatar

Joined: Fri Apr 27, 2012 6:49 am
Posts: 40
Be aware that it's not uncommon for new energy efficient dry type transformers (15-500 kVA) to have inrush factors in the 15-20 range.

When purchasing a new transformer, ask the manufacturer for the specific information.

When analyzing an existing facility, 12 is a good assumption. If there were actual inrush problems, it would be apparent and someone would be making some noise about it. I wouldn't recommend pointing out inrush problems according to the software in an existing facility where there are no real life inrush problems.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883