bruinfan wrote:
I would like to know what the consensus is for coordinating the upstream protection device with both the 3-phase and unbalanced damage curve of the downstream transformer? Someone mentioned to me the other day to just coordinate the device with the 3-phase damage curve only. This does not seems okay with me. Any thoughts?
The ANSI C57 Thru Fault curves that you are referring to have a 0.577 shift to the left for line-ground faults on the secondary of a delta-wye connected transformer and 0.866 shift to the left of line-line faults on the secondary of a delta-delta transformer.
The problem is that for each of these unbalanced faults on the secondary side, a secondary winding can experience it's maximum short circuit current and need cleared based on the ANSI curve. On the primary side of the transformer, the primary protective devices are seeing less current on the order of 0.577 or 0.866 depending on the winding. It is best if the time-current curve of your primary protective device can pass to the left of the 'adjusted' ANSI curve as much as possible.
It is usually difficult to pass to the left of the entire adjusted curve so you do the best you can. Having a secondary device's curve pass to the left of the adjusted curve is also helpful. Look at the curve and you will see a change in slope. This occurs at 6X the transformers full load current and is usually considered more of an overload problem than a short circuit problem at that level.