 Post subject: Disconnection times (t)
PostPosted: Fri Nov 16, 2012 2:47 am 
User avatar

Joined: Wed Oct 17, 2012 1:59 am
Posts: 7
I would like clarification as to to what value should be taken for circuit protection disconnection times. My understanding is that it ought to be I (bf) but reconsidering the calculations again I am now not sure whether it is considered that it ought to be the total arcing current Total I(a).
Please advise.

Another comment I would make is that the Arc Flash Calculation guide omits to make reference to fuses as circuit protectors. I would like to see in future revisions of this excellent publication references and diagrams for at least the common standard BS88 HRC fuses.

thanks


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Nov 16, 2012 6:35 am 
Sparks Level

Joined: Thu Jul 07, 2011 6:03 am
Posts: 64
Location: Netherlands
The disconnection time for calculating arc flash hazard according to IEEE 1584 has to be determined from the arcing current Ia. Additionally for voltages under 1000V it also has to be calculated at 85% Ia, calculate the hazard for both cases and take the highest incident energy as a result.

The arcing current can be a lot lower than the bolted fault current and could for example result in a fast acting stage of a protection to no longer trip as expected, leading to (very) high results.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Nov 19, 2012 6:52 pm 
Sparks Level

Joined: Sat Apr 04, 2009 9:50 pm
Posts: 104
Location: San Antonio, TX
I agree with jvrieling


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883