PostPosted: Mon Mar 11, 2013 9:23 am 

Joined: Mon Mar 11, 2013 9:16 am
Posts: 4
Hi all,
I'm trying to determine the AF level at the breaker for a 4.5 MVA synchrounous generator.

With the utility isolated, I can calculate the level on the gen side of the breaker by using the generator decrement curve and fixing the time at 2 seconds, however, if I then connect the utility, I get significantly more fault current for the full two seconds even though differential protection would remove the utility contribution in a few cycles.

Is there a way to combine contributions from a decrement curve for two seconds and a utility source for a specified duration when calculating an arc flash level?

I'm using ETAP 12.

Thanks


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Mar 13, 2013 8:30 am 

Joined: Mon Mar 11, 2013 9:16 am
Posts: 4
Can anyone help me with this?

The short version of the question is can ETAP calculate incident energy and boundaries based on different clearing times from multiple sources, and if not, is it permissible to do it by hand and how.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Mar 13, 2013 2:06 pm 
Plasma Level
User avatar

Joined: Wed May 07, 2008 5:00 pm
Posts: 822
Location: Rutland, VT
I don't know if ETAP has a feature like EasyPower that is called the Integrated method. The Integrated method takes into account the decreasing currents from motors and generators and also from multiple sources being switched out through protective devices tripping. Did you ask ETAP or look at the Help file?

_________________
Barry Donovan, P.E.
www.workplacesafetysolutions.com


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Mar 14, 2013 2:11 pm 

Joined: Mon Mar 11, 2013 9:16 am
Posts: 4
I know it can integrate decrements curves from generators, but the multiple sources is the question. I haven't seen anything in the help file.
I might have to contact ETAP.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Mar 15, 2013 11:01 am 

Joined: Mon Mar 11, 2013 9:16 am
Posts: 4
ETAP recommended to create a dummy relay/breaker to set the clearing time on the generator side of the breaker to 2 seconds, then enable the subtraction of incident energy for multiple sources in the preferences menu.

This did the trick. Now I've got 2 seconds of contribution from the generator, and 0.103 seconds of contribution from the utility combined.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883