 Post subject: Cable Length Accuracy
PostPosted: Wed Dec 31, 2008 8:41 am 

Joined: Wed Nov 12, 2008 7:02 am
Posts: 2
Are there any guidelines as to how accurate cable lengths should be when conducting arc flash study? It seems the be that cables usually have a relatively low impedance when compared with transformers, especially when dealing larger cables. When plants don't have decent drawings, collecting cable lenghts can be quite time consuming. Is eyeballing it to get a relative length sufficient?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Dec 31, 2008 3:39 pm 
Sparks Level

Joined: Thu Oct 18, 2007 7:10 pm
Posts: 261
Location: NW USA
Estimating length is as good as is possible. Choose a method that works for you whether that be be pacing-off or measuring the length on the surface for underground runs, or measuring from plan drawings; with added footage for the risers into equipment.

Consider that adding cable length will at some point cause risk category to go UP if the added impedance causes instantaneous trip setting to not pick up. That particular footage of cable length can have a dramatic effect on arc flash calculated exposure.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883