 Post subject: Modeling for a Fused Disconnect
PostPosted: Thu Dec 05, 2013 12:16 am 
User avatar

Joined: Thu Sep 24, 2009 5:46 pm
Posts: 25
Is there a recommended gap for 600VAC fused disconnects (safety switches)? ETAP uses 25 for a panel board an 32 for a switchboard.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Dec 05, 2013 5:44 am 
Plasma Level
User avatar

Joined: Wed May 07, 2008 5:00 pm
Posts: 822
Location: Rutland, VT
I know that EasyPower uses 32mm for a switch.

_________________
Barry Donovan, P.E.
www.workplacesafetysolutions.com


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Dec 05, 2013 7:11 am 
User avatar

Joined: Thu Sep 24, 2009 5:46 pm
Posts: 25
wbd wrote:
I know that EasyPower uses 32mm for a switch.


WBD,

Does Easy Power default to a 24" working distance for this?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Dec 05, 2013 7:40 am 
Sparks Level
User avatar

Joined: Wed Jun 10, 2009 5:00 pm
Posts: 263
Location: Toronto
Quote:
Is there a recommended gap for 600VAC fused disconnects (safety switches)? ETAP uses 25 for a panel board an 32 for a switchboard.


Please check http://www.arcadvisor.com/arcflash/ieee1584.html#Equipment for typical conductor gaps. Please note these are typical but not 'recommended' gaps. I would use actual gap for the analysis.

_________________
Michael Furtak, C.E.T.
http://arcadvisor.com


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Dec 06, 2013 6:34 am 
Plasma Level
User avatar

Joined: Wed May 07, 2008 5:00 pm
Posts: 822
Location: Rutland, VT
You can set the working distance to what you want but the default is still 18" for 600V and less. This would consistent with working on these circuits with the proper PPE

_________________
Barry Donovan, P.E.
www.workplacesafetysolutions.com


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Dec 11, 2013 3:09 am 
User avatar

Joined: Thu Sep 24, 2009 5:46 pm
Posts: 25
Does someone have a copy of UL 98 and could look up the bus spacing?


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 6 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883