ekstra   ara
 Post subject: 208V equipment fed from 750kva 600/208V transformer
PostPosted: Fri Jan 30, 2009 10:42 am 

Joined: Fri Jan 30, 2009 10:04 am
Posts: 10
Location: Toronto
I am a new member. Please let me post a question.
IEEE 1584 states:"Equipment below 240v need not be considered unless it involves at least one 125kva or larger low impedance transformer in its IMMEDIATE supply"
My case: 750kVA 600/208-120V 7.1% transformer supplys 208V switchboard A. Switchboard A supplys 208V panel B via cables, and panel B supplys another 208V panel C via cables. I need to do arc flash analysis for switch board A based on IEEE 1584. Do I need to do arc flash analysis for panel B and C? Or just label panel B and C according to NFPA 70 table 130.7(C)(9)(a)? I do not think the 750kva transformer is immediate supply to panel B. C. Thanks!


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Apr 20, 2009 8:37 pm 
Sparks Level

Joined: Sat Apr 04, 2009 9:50 pm
Posts: 104
Location: San Antonio, TX
I don't think that the transformer is Panel B or C immediate power supply. I understand that the calculation is not necessary.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Apr 21, 2009 1:13 pm 
Arc Level

Joined: Tue Jan 13, 2009 5:00 pm
Posts: 532
The same standard says "The arc-flash hazard need only be considered for large 208 V systems: systems fed by transformers smaller than 125 kVA should not be a concern." No "immediate" qualifier there. Also note that NFPA avoids the "immediate" qualifier.

Also see [url="http://www.arcflashforum.com/showthread.php?t=324"]http://www.arcflashforum.com/showthread.php?t=324[/url]


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Apr 21, 2009 4:30 pm 
Arc Level

Joined: Thu Jan 10, 2008 8:49 pm
Posts: 498
Location: New England
YOU don't have to list the the HRC Task Matrix. Since it is outside the analysis,, you can just list a single HRC of 1 or 0 for all tasks.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883