 Post subject: 1000 second clearing time
PostPosted: Mon Feb 09, 2009 11:49 am 

Joined: Tue Mar 25, 2008 1:00 pm
Posts: 32
Is there really any way a 480V panel fed by a 700kva trans is going to sit there and arc for 1000 seconds? It's got a 1600A breaker but the software is telling me its only seeing 350A fault, so its not tripping. How realistic is this?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Feb 09, 2009 1:14 pm 
Arc Level

Joined: Wed Jun 04, 2008 9:17 am
Posts: 428
Location: Spartanburg, South Carolina
deprico wrote:
Is there really any way a 480V panel fed by a 700kva trans is going to sit there and arc for 1000 seconds? It's got a 1600A breaker but the software is telling me its only seeing 350A fault, so its not tripping. How realistic is this?

Rated current on a 700 kVA (odd size!) transformer is 842A at 480V. The fault current is not reasonable.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Feb 10, 2009 5:53 pm 
Arc Level

Joined: Thu Jan 10, 2008 8:49 pm
Posts: 498
Location: New England
1600A MCB is a bit oversized. Does it have a rating plug by which you can change the trip value. A trip value of 1200 or even 1000 amps would shift your trip curve. Even without this, your transformer should be 5 to 6% impedance, which means your fault current should be 15,000 amps. With a finite bus around 10 to 12 thousand amps. So you have something wrong.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Feb 10, 2009 8:37 pm 
Arc Level

Joined: Wed Jun 04, 2008 9:17 am
Posts: 428
Location: Spartanburg, South Carolina
Maybe the software is looking at the incident energy on the line side of the MCB and is reporting the current in a protective device on the primary of the transformer.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Feb 26, 2009 8:03 pm 
Sparks Level

Joined: Thu Oct 18, 2007 7:10 pm
Posts: 261
Location: NW USA
deprico wrote:
Is there really any way a 480V panel fed by a 700kva trans is going to sit there and arc for 1000 seconds? It's got a 1600A breaker but the software is telling me its only seeing 350A fault, so its not tripping. How realistic is this?


If the software is saying 350A fault, I assume there is a length of feeder cable that should be protected by a small circuit breaker. I suspect you are missing a circuit breaker from your study (just guessing).

Gary B


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Feb 27, 2009 7:20 am 

Joined: Mon Dec 08, 2008 7:13 am
Posts: 26
Location: Quebec, Canada
jghrist wrote:
Maybe the software is looking at the incident energy on the line side of the MCB and is reporting the current in a protective device on the primary of the transformer.


Deprico: If you're using Easypower, jghrist found your problem. That's just how it presents the results.

See the report «Upstream Trip Device Name».


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 6 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883