deprico wrote:
Say I look at the AIC rating on 480V panel and find 65k. For many tasks found in the tables, Note 1 is called out stating that the PPE level provided is suitable for available short circuit current less than 25k.
If I want to take the cover panel off, do some thermography, and replace the cover, what PPE do I wear? It appears to be I can't use the tables!
Probally not, but AIC is not the same as available fault current as I am sure you know. You need the available fault current and clearing time of the protective device to determine if you can use the tables.