Post subject: Open Delta Modeling Posted: Fri Jul 18, 2014 11:49 am |
|
Joined: Wed Mar 13, 2013 9:12 am Posts: 12
|
|
Hello,
I have a service fed by 2 - 100kVA transformers set up as an open delta. The primary side is connected as a grounded wye at 46kV and the secondary is a open delta with a center tap. The secondary voltages are then 120/240 and 208. How would you model this for arc flash hazard?
|
|
| Top |
|
 |
|
arcad
|
Post subject: Re: Open Delta Modeling Posted: Thu Jul 24, 2014 9:23 am |
|
| Sparks Level |
 |
Joined: Wed Jun 10, 2009 5:00 pm Posts: 271 Location: Toronto
|
|
For arc flash analysis, I would model it as a full delta with 240V phase to phase voltage.
|
|
| Top |
|
 |
|