| Author: | Polar [ Fri Jul 18, 2014 11:49 am ] |
| Post subject: | Open Delta Modeling |
Hello, I have a service fed by 2 - 100kVA transformers set up as an open delta. The primary side is connected as a grounded wye at 46kV and the secondary is a open delta with a center tap. The secondary voltages are then 120/240 and 208. How would you model this for arc flash hazard? |
|
| Author: | arcad [ Thu Jul 24, 2014 9:23 am ] |
| Post subject: | Re: Open Delta Modeling |
For arc flash analysis, I would model it as a full delta with 240V phase to phase voltage. |
|