I'm attempting to get utility data for a project in China and, as you can imagine, it's been difficult - and not just because of the language barrier. They are saying they do not have single line to ground fault data or SLG X/R ratio because there is no ground. Is this true? I thought the utility always carried a ground and would know what it's 1ph fault contribution would be.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Utility Information
PostPosted: Mon Aug 25, 2014 7:52 am 
Sparks Level

Joined: Thu Jul 07, 2011 6:03 am
Posts: 64
Location: Netherlands
Why couldn't it be ungrounded? Where I live a lot of medium voltage distribution systems are ungrounded, although it's being phased out for HRG.

For your model simply enter 0 MVA as line to ground contribution, your calculation will simply use the ungrounded constant for incident energy (at least SKM does). If I can't get utility data I typically use ungrounded as an assumption since it's the worst-case and has no influence on the low voltage calculations, the impact of MV grounding is not that big on arc flash results.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883