It is currently Fri Nov 06, 2026 9:01 am
 Post subject: 1000 second clearing time
PostPosted: Mon Feb 09, 2009 11:49 am
Is there really any way a 480V panel fed by a 700kva trans is going to sit there and arc for 1000 seconds? It's got a 1600A breaker but the software is telling me its only seeing 350A fault, so its not tripping. How realistic is this?
PostPosted: Mon Feb 09, 2009 1:14 pm
Rated current on a 700 kVA (odd size!) transformer is 842A at 480V. The fault current is not reasonable.
PostPosted: Tue Feb 10, 2009 5:53 pm
1600A MCB is a bit oversized. Does it have a rating plug by which you can change the trip value. A trip value of 1200 or even 1000 amps would shift your trip curve. Even without this, your transformer should be 5 to 6% impedance, which means your fault current should be 15,000 amps. With a finite bus around 10 to 12 thousand amps. So you have something wrong.
PostPosted: Tue Feb 10, 2009 8:37 pm
Maybe the software is looking at the incident energy on the line side of the MCB and is reporting the current in a protective device on the primary of the transformer.
PostPosted: Thu Feb 26, 2009 8:03 pm
If the software is saying 350A fault, I assume there is a length of feeder cable that should be protected by a small circuit breaker. I suspect you are missing a circuit breaker from your study (just guessing).
Gary B
PostPosted: Fri Feb 27, 2009 7:20 am
Deprico: If you're using Easypower, jghrist found your problem. That's just how it presents the results.
See the report «Upstream Trip Device Name».
