 Post subject: Utility provided system impedances
PostPosted: Wed Jun 03, 2015 12:29 pm 

Joined: Tue Jun 02, 2015 11:32 am
Posts: 2
Good Day,

We were provided utility data, but it only included system impedances (R1,X1,R0,X0-PU on 100MVA Base). The utility company considers providing the fault current values a liability. What is the recommended method, convert to SC amps (reference Jim Phillips article, Making Sense of the Numbers, Utility Company Short-circuit Data For Arc Flash Studies) or input directly into software as ‘Zpu’ fault duty units, or other method. Will each method yield the same results? Thanks - DBL


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Utility provided system impedances
PostPosted: Wed Jun 03, 2015 6:05 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1504
Location: Scottsdale, Arizona
DBL wrote:
Good Day,

The utility company considers providing the fault current values a liability.

That is a pretty interesting statement from the utility. The impedance data and the short circuit data are pretty much the same thing - just need a few calculations to go from one to the other. The article that you reference did not have a case with Z0. That is used when there is a ground/non-phase path so....

For a line-to-ground fault:
I line-to-ground = (3xV) / (Z1 + Z2 + Z0) in your case (and in almost every case Z2 is the same as Z1)
I line-to-ground = (3xV) / (2xZ1 + Z0)

I show everything as a magnitude Z to make it simple. You have the better format of individual R and X values.

The utility indirectly gave you the fault current. It is a direct function of the equivalent impedance which they gave you. Many utilities simply shroud this information in legal disclaimers and go ahead and provide it.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Utility provided system impedances
PostPosted: Mon Jun 08, 2015 4:10 am 

Joined: Tue Jun 02, 2015 11:32 am
Posts: 2
Thanks Jim.
To confirm, one can obtain Z with individual R and X values, using Z=SQRT[R squared + X squared].


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Utility provided system impedances
PostPosted: Mon Jun 08, 2015 7:04 am 

Joined: Mon Nov 10, 2014 11:01 am
Posts: 22
For some programs you have to enter per unit impedance. I developed a spreadsheet to convert to Per Unit impedance. I tried to paste the spreadsheet
but it was unreadable. I will be happy to provide it.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Utility provided system impedances
PostPosted: Mon Jun 08, 2015 7:13 am 
Sparks Level

Joined: Fri Apr 15, 2011 7:43 am
Posts: 177
Location: Colorado
I would rather have the impedance values, most of the time I only get a fault current.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883