 Post subject: Which is the correct way to measure conductor gap
PostPosted: Fri Jan 29, 2016 9:25 am 

Joined: Fri Aug 03, 2012 1:44 am
Posts: 9
Which is the correct way to measure the conductor gap?
Based on Figure 5 of IEEE 1584-2002 seems that it correspond to:
- Bus bar center line spacing
- Gap between buses and back wall of box

And what about distance between cables and MCC boxes?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Which is the correct way to measure conductor gap
PostPosted: Fri Jan 29, 2016 11:51 am 
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 2178
Location: North Carolina
I always thought conductor gap was just that...edge to edge. What we'd really like is arc length but since this is so hard to predict they settled for conductor gap, measured edge-to-edge.