| Which is the correct way to measure conductor gap https://brainfiller.com/arcflashforum/viewtopic.php?f=23&t=3851 |
Page 1 of 1 |
| Author: | Giovanni G [ Fri Jan 29, 2016 9:25 am ] |
| Post subject: | Which is the correct way to measure conductor gap |
Which is the correct way to measure the conductor gap? Based on Figure 5 of IEEE 1584-2002 seems that it correspond to: - Bus bar center line spacing - Gap between buses and back wall of box And what about distance between cables and MCC boxes? |
| Author: | PaulEngr [ Fri Jan 29, 2016 11:51 am ] |
| Post subject: | Re: Which is the correct way to measure conductor gap |
I always thought conductor gap was just that...edge to edge. What we'd really like is arc length but since this is so hard to predict they settled for conductor gap, measured edge-to-edge. |