It is currently Fri Oct 23, 2026 1:58 am
 Post subject: Modeling PDUs
PostPosted: Fri Jul 31, 2026 8:59 am
How do you guys typically model PDUs? Do you model each component like an individual component? do you model the wiring in-between?
For example, a recent project includes an IT floor with CRACs, PDUs, and server equipment. A typical trunk might include a distribution panel feeding a number of PDUs, which comprise a 480V, 200A breaker>few feet of conductor>transformer>two "panel" main 225A breakers>misc. branch circuit breakers, including one 3-pole 100a breaker which feeds a subsequent panel 20'-150' away.
I'm inclined to model each component, however the PDU transformers have no impedance numbers on their nameplates. I know transformers of that size typically range from 2-5%, but I've also heard that PDU transformers tend to have lower impedances.
Do you guys typically model every component or treat them as a single component?
 Post subject: Re: Modeling PDUs
PostPosted: Fri Jul 31, 2026 12:47 pm
Every component...
Mike
PostPosted: Fri Aug 07, 2026 1:31 pm
Every component. I've not seen a PDU with isolation so you'll likely label with the worst case IE and the highest voltage.
PostPosted: Wed Aug 12, 2026 12:07 pm
Thanks, guys. So question: What do you consider an appropriate estimation for impedance? Despite being a well-known brand of PDU, the transformers do not list impedance. I'm hesitant to estimate for impedance because it has such an outsized effect on incident energy.
PostPosted: Wed Aug 12, 2026 12:14 pm
Here's an example photo of what I'm talking about.
File comment: Here's an example.
PostPosted: Thu Aug 13, 2026 5:49 am
What I've done in these cases is either:
1) Ask the customer for a submittal. If that is a dead end;
2) Assume an impedance and document that in the report. There are a number of references for impedance estimates you can use for dry types.
Mike