 Post subject: Standby Diesel Generator
PostPosted: Tue Jan 09, 2018 11:02 am 

Joined: Tue Jan 09, 2018 10:59 am
Posts: 2
I have to model a standby generator 200 KW and was given a fault current value from the manufacturer of around 7.6 kA. Can I just model a grid with this kA value and simulate the arc flash situation on emergency power? I am using ETAP.

Thanks!


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Standby Diesel Generator
PostPosted: Sat Jan 13, 2018 7:28 am 
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 2174
Location: North Carolina
akjoseph_77 wrote:
I have to model a standby generator 200 KW and was given a fault current value from the manufacturer of around 7.6 kA. Can I just model a grid with this kA value and simulate the arc flash situation on emergency power? I am using ETAP.

Thanks!


For short circuit purposes, yes. Otherwise there are reasonable approximate values for the primary and secondary (X' and X'') that can be used for arc flash calculations where ETAP uses piecewise modelling to account for the long asymmetrical fault currents. This is always a tricky situation because the available fault current is usually about an order of magnitude less than utility fault current which greatly increases the overcurrent trip times and makes incident energy values much higher than during normal operation.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Standby Diesel Generator
PostPosted: Fri Mar 09, 2018 10:47 pm 

Joined: Fri Mar 09, 2018 10:34 pm
Posts: 1
Standby diesel generator 200KW 250KVA, the rated current should be 360 (A). To ensure safety, please consult technician at this website:

_________________
Life is an attitude.


Last edited by wbd on Sat Mar 10, 2018 6:25 am, edited 1 time in total.
deleted link to commercial website


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Standby Diesel Generator
PostPosted: Sat Mar 10, 2018 6:27 am 
Plasma Level
User avatar

Joined: Wed May 07, 2008 5:00 pm
Posts: 822
Location: Rutland, VT
Quote:
Standby diesel generator 200KW 250KVA, the rated current should be 360 (A).


Yes but the OP was asking about modeling for short circuit and not looking for FLA

_________________
Barry Donovan, P.E.
www.workplacesafetysolutions.com


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883