 Post subject: DC Arc Flash Calculation for Arc Flash Boundary
PostPosted: Thu Jan 17, 2019 3:39 pm 

Joined: Mon Aug 25, 2014 3:11 pm
Posts: 2
I am preforming DC arc flash calculations for a system with a reactor having the following ratings: 250VDC, 1000A, 262.5KVA, and 4.05%Z. I have calculated the incident energy using NFPA 70E-2015 Section D.5 for the Maximum Power Method and looking to find the Arc Flash Boundary. Is it acceptable to use the Ralph Lee Calculation Method equation D.2.1(d) or (e) for determining the distance?, if so what "t" (time of arc exposure) would be used?

Thanks in advance.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: DC Arc Flash Calculation for Arc Flash Boundary
PostPosted: Thu Jan 17, 2019 3:43 pm 

Joined: Mon Aug 25, 2014 3:11 pm
Posts: 2
I have found the linked spread sheet below online with AFB calculated, but because it is locked I cannot see the equation used. Based on using the Ralph Lee Method for my calculations I cannot come to the same conclusions as the spread sheet.

http://efcog.org/wp-content/uploads/2016/11/DC-Arc-Flash-Calculator-EFCOG-ESW-DC-SC.xlsx


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: DC Arc Flash Calculation for Arc Flash Boundary
PostPosted: Fri Jan 18, 2019 5:30 pm 
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 2178
Location: North Carolina
rlorenz2 wrote:
I am preforming DC arc flash calculations for a system with a reactor having the following ratings: 250VDC, 1000A, 262.5KVA, and 4.05%Z. I have calculated the incident energy using NFPA 70E-2015 Section D.5 for the Maximum Power Method and looking to find the Arc Flash Boundary. Is it acceptable to use the Ralph Lee Calculation Method equation D.2.1(d) or (e) for determining the distance?, if so what "t" (time of arc exposure) would be used?

Thanks in advance.


Shouldn't be that hard since its basically a linear equation except for the D^2 term. Did you try solving it directly yourself?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: DC Arc Flash Calculation for Arc Flash Boundary
PostPosted: Fri Aug 02, 2019 10:50 am 

Joined: Tue Mar 05, 2019 5:47 am
Posts: 14
I will reuse this topic.

Has anyone did DC arc flash for MV systems eg.rail 3kV ? I found only J.C.Das publication where he use S-O equations and I think at the end it was stated that it can be extended with reasonable results. I think S-O doesn't specify voltage limits for model but testing was done max at 1000VDC ( or 1200VDC).

I haven't seen this in any software yet
Any updates on this ?


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883