 Post subject: Comparing 1584/2002 to 1584/2018 (existing studies)
PostPosted: Mon Feb 18, 2019 1:37 pm 
Sparks Level

Joined: Sat Nov 21, 2009 10:23 pm
Posts: 124
Location: Ohio
Just checking with those that have had a chance to compare an existing 480V study with the same study done in 1584/2018. I run Easy Power and I have taken a couple of studies that were run in 1584/2002 and changed the electrode config to either Barrier or Horizontal, everything else was left in the default mode. In all cases the 1584/2018 IE results are 25% to 35% of original findings done with the 1584/2002 version.

Is this what everyone else finding, especially those running SKM and ETAP


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Comparing 1584/2002 to 1584/2018 (existing studies)
PostPosted: Tue Feb 19, 2019 9:32 am 

Joined: Tue May 29, 2018 8:19 am
Posts: 45
I've seen both higher and lower. See the thread on "Low arcing current" for one case comparison.

_________________
Alan Lehman


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Comparing 1584/2002 to 1584/2018 (existing studies)
PostPosted: Fri Feb 22, 2019 12:23 am 

Joined: Mon Jun 05, 2017 8:07 pm
Posts: 15
Flash wrote:
Just checking with those that have had a chance to compare an existing 480V study with the same study done in 1584/2018. I run Easy Power and I have taken a couple of studies that were run in 1584/2002 and changed the electrode config to either Barrier or Horizontal, everything else was left in the default mode. In all cases the 1584/2018 IE results are 25% to 35% of original findings done with the 1584/2002 version.

Is this what everyone else finding, especially those running SKM and ETAP



Yes it is possible, The arc current variation with selection of Conductors VCBB or HCB may yield those differences. The arc current variation is also considered for medium voltage studies which was not considered in the IEEE 1584-2002 standard

Regards
Raghu


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883