ekstra   ara
 Post subject: Unbalanced delta
PostPosted: Mon Dec 30, 2019 3:56 pm 
Arc Level

Joined: Tue Jan 13, 2009 5:00 pm
Posts: 532
Customer is served with two 50s and a 100 kVA transformer. The 100 kVA is center tapped and grounded to serve the single phase loads. The customer asks for "actual" fault current at the secondary terminals. The only software on hand provides for balanced sources only. How would you go about calculating this by hand? Do you know of any good references? Thanks.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Unbalanced delta
PostPosted: Thu Jan 23, 2020 7:22 am 

Joined: Thu Jan 23, 2020 7:12 am
Posts: 1
stevenal wrote:
Customer is served with two 50s and a 100 kVA transformer. The 100 kVA is center tapped and grounded to serve the single phase loads. The customer asks for "actual" fault current at the secondary terminals. The only software on hand provides for balanced sources only. How would you go about calculating this by hand? Do you know of any good references? Thanks.


I'm in pretty much the same situation. Did you ever find a solution?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Unbalanced delta
PostPosted: Thu Jan 23, 2020 8:49 am 
Arc Level

Joined: Tue Jan 13, 2009 5:00 pm
Posts: 532
Thanks for the bump. No, I have not found an answer.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Unbalanced delta
PostPosted: Sat Jan 25, 2020 5:12 am 
Plasma Level
User avatar

Joined: Wed May 07, 2008 5:00 pm
Posts: 822
Location: Rutland, VT
What software are you using? Have you reached out to their tech support for suggestions?

_________________
Barry Donovan, P.E.
www.workplacesafetysolutions.com


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Unbalanced delta
PostPosted: Mon Jan 27, 2020 9:54 am 
Arc Level

Joined: Tue Jan 13, 2009 5:00 pm
Posts: 532
I use Aspen Oneliner, which can model three phase transformers and systems only. I have not asked support, since it is clearly outside the software's scope. Perhaps Distriview might work, but its not in the budget. The inquiries are rare enough that hand calculations should suffice if I understood just how to perform them.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883