 Post subject: Multiple disconnects in single enclosure
PostPosted: Tue Mar 10, 2020 9:32 am 

Joined: Tue Mar 10, 2020 9:19 am
Posts: 4
I'm trying to figure out how to model a portion of this system. A contractor has recently installed four new motor feeders, and they all pass through a single disconnect enclosure. Each feeder has a 400A breaker at the MCC, and they each also have a 400A breaker in this new enclosure. I imagine the incident energy to be higher than the worst case for any single feeder, but don't think I should add them all together either. Has anybody dealt with something similar?

It looks more or less like this:
Code:
................................
:     |     |     |     |      :
:     |     |     |     |      :
:      )     )     )     )     :
:     |     |     |     |      :
:     |     |     |     |      :
................................


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Multiple disconnects in single enclosure
PostPosted: Tue Mar 10, 2020 12:35 pm 
Plasma Level
User avatar

Joined: Wed May 07, 2008 5:00 pm
Posts: 822
Location: Rutland, VT
What software are you using? An arc on any one of the breakers would expand to include all the others. One way is to model the enclosure as a bus on the load side of all the breakers and then fault that bus. I use EasyPower so the bus would be set to ignore the main breakers, on Integrated method and that would give you the incident energy for that box.

_________________
Barry Donovan, P.E.
www.workplacesafetysolutions.com


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Multiple disconnects in single enclosure
PostPosted: Wed Mar 11, 2020 5:59 am 

Joined: Tue Mar 10, 2020 9:19 am
Posts: 4
wbd wrote:
What software are you using? An arc on any one of the breakers would expand to include all the others. One way is to model the enclosure as a bus on the load side of all the breakers and then fault that bus. I use EasyPower so the bus would be set to ignore the main breakers, on Integrated method and that would give you the incident energy for that box.


I am also using EasyPower.

That is how we approach most enclosures, but this equipment has several motors and control panels below it. I don't want to erroneously affect the IE at those panels. Maybe I'll run that as a scenario and see if anything changes significantly.

Thanks for the help.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Multiple disconnects in single enclosure
PostPosted: Thu Mar 12, 2020 6:11 am 
Plasma Level
User avatar

Joined: Wed May 07, 2008 5:00 pm
Posts: 822
Location: Rutland, VT
Yes you will have to do a separate analysis for the common enclosure and then do another for the equipment downstream with each feed as it is from the common enclosure.

_________________
Barry Donovan, P.E.
www.workplacesafetysolutions.com


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Multiple disconnects in single enclosure
PostPosted: Thu Mar 12, 2020 9:41 am 

Joined: Tue Mar 10, 2020 9:19 am
Posts: 4
Does EasyPower have an easy way to do that, or would that have to be done manually?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Multiple disconnects in single enclosure
PostPosted: Fri Mar 13, 2020 6:33 am 
Plasma Level
User avatar

Joined: Wed May 07, 2008 5:00 pm
Posts: 822
Location: Rutland, VT
You would have to model it twice but that is not hard. One model would be with the single enclosure with all 4 breakers connected to a bus. The other with the system as it normally is. The single connected bus model would give you the incident energy for that enclosure.

Are all 4 breakers in the enclosure fed from the same bus or multiple different buses?

_________________
Barry Donovan, P.E.
www.workplacesafetysolutions.com


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Multiple disconnects in single enclosure
PostPosted: Fri Mar 13, 2020 7:27 am 

Joined: Tue Mar 10, 2020 9:19 am
Posts: 4
They are all fed from individual 400A breakers on the same MCC bus.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 7 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883